Scantonic 9651 fire alarm


Jason Edmonds

Recommended Posts

Greetings all, need some help and advice plz.

A friend of mine has a scantronic 9651 with smoke detectors fitted. The problem is he would an electronic sounder fitted because it only bleeps at the keypad. Is there a way to fit say a 12v roshni to the panel via the 12v aux or the n/o-n/c contacts.

thanks in advance 

Link to comment
Share on other sites

There is already a speaker output on the 9651 which will produce many tones including a distinctive one for the fire alarm.

You can have up to two speakers so ideal for hallway and 1st floor. The output is marked LS + or SPKR depending on version. They are always next to the siren outputs.

 

Suitable speaker - http://cpc.farnell.com/lynteck/ly07-009-37/extension-speaker/dp/SR04341

 

Don't bother trying to connect anything to the detectors themselves as it won't be re-settable from the panel and will drive them mad.

 

However, although approved under certain circumstances bear in mind this sort of setup is more vulnerable to failure in a fire situation of through neglect of the alarm system eg. system batteries.

 

 

So, I've decided to take my work back underground.... to stop it falling into the wrong hands

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.