Hi,

 

For a new build, I'm going to be installing a fully wired Texecom Premier Elite as the burglar alarm. Just wondering what people's thoughts are on using it also as a Fire Alarm/Detection system and how to deal with the sounders. It is for a large house (over 200Sqm per floor).

 

My issue is mainly regarding the numerous sounders needed, the installation will  have about 10 - 15 smoke detectors to meet the LD2 system required.

 

All Texecoms wired detectors appear to not include a sounder (other than their wireless one). Does anyone have a good solution to this - i.e. know of other wired smoke/Co2/heat detectors which would be suitable for the Premier Elite and also include a loud speaker and ideally being total of 4 wire or less (if even possible) so that it can use FP200 4 core cable?

 

I could put sounders just in the landing spaces, but my worry is that this wouldn't be loud enough.

 

Mike

 

Link to comment
Share on other sites

3 minutes ago, MrHappy said:

get a proper fire or proper interlinked smoke alarms

Thought about that...is it for the issues I've mentioned or due to complexity/reliability with combining it into the Premier?

Here's the issues with a separate or interlinked  ...

 

Interlinked unfortunately is not allowed due to building regs (as each floor is over 200SqM, it has to have central control panel). Whilst Building Control have said they will allow such in my instance, the electricians will not sign such off. Other than not knowing where the fire is with interlinked, I think interlinked has huge pro's in terms of no single point of failure and a siren for each detector. Nest is an option for area notification, but I'd have to consider the mains wiring being that the electricians will not sign this off.
 

In regards to a separate central system for Fire only, I like the Texecom solution as I'll have keypads dotted around so would get a quick visual on where the fire is without having to go to the central fire panel (which will likely be in a closet). 

 

Feels like quite a dilemma - surely this isn't too un-common and there's a great solution out there ??

 

 

 

Link to comment
Share on other sites

52 minutes ago, MrHappy said:

get a proper fire or proper interlinked smoke alarms

 

I could install a few sound bombs which would be much louder (and I think is intermittent sound for fire). 

Your comment seems to suggest it's perhaps not a good idea to use the Premier though as a 'proper' fire alarm system - would be keen to hear what your reasons are, I do want it to be a good (and very robust) system, but ideally with quick identification of where the fire is.

 

Thanks

Link to comment
Share on other sites

2 hours ago, Michaelangelo999 said:

 

I could install a few sound bombs which would be much louder (and I think is intermittent sound for fire). 

Your comment seems to suggest it's perhaps not a good idea to use the Premier though as a 'proper' fire alarm system - would be keen to hear what your reasons are, I do want it to be a good (and very robust) system, but ideally with quick identification of where the fire is.

 

Thanks

Proper fire alarm kit isn't that expensive

 

Then us a relay output to trigger the prem

  • Upvote 1
Link to comment
Share on other sites

3 hours ago, Michaelangelo999 said:

Thought about that...is it for the issues I've mentioned or due to complexity/reliability with combining it into the Premier?

Here's the issues with a separate or interlinked  ...

 

Interlinked unfortunately is not allowed due to building regs (as each floor is over 200SqM, it has to have central control panel). Whilst Building Control have said they will allow such in my instance, the electricians will not sign such off. Other than not knowing where the fire is with interlinked, I think interlinked has huge pro's in terms of no single point of failure and a siren for each detector. Nest is an option for area notification, but I'd have to consider the mains wiring being that the electricians will not sign this off.
 

In regards to a separate central system for Fire only, I like the Texecom solution as I'll have keypads dotted around so would get a quick visual on where the fire is without having to go to the central fire panel (which will likely be in a closet). 

 

Feels like quite a dilemma - surely this isn't too un-common and there's a great solution out there ??

 

 

 

Get another electrician to sign off or do the interlinked bit 

 

Total blag , what's reason they won't sign off an Interlinked system ? They only signing of electrical part , all down ra , where's doc cubit 

  • Upvote 1
Link to comment
Share on other sites

7 hours ago, Michaelangelo999 said:

Your comment seems to suggest it's perhaps not a good idea to use the Premier though as a 'proper' fire alarm system - would be keen to hear what your reasons are,

 

Its not fit for purpose,

 

7 hours ago, Michaelangelo999 said:

I do want it to be a good (and very robust) system, but ideally with quick identification of where the fire is.

 

analogue addressable fire alarm system, if you've a half decent architect or project manager you'll should have already been advised of this

  • Upvote 1

Mr? Veritas God

Link to comment
Share on other sites

Thanks all for your comments,

 

The electrician's said they won't sign it off as they will only do work which conforms to building regs regardless if Building Control approve a variation. I thought they just effectively signed off Part P and not Part B. Potentially they're creating less work for themselves as they would not necessarily be fitting the centralized fire alarm (just power to it), yet they would have been fitting the interlinked cable otherwise. 

 

I think separate panel it is (and as al-yeti says - linked to the Premier) .. any recommendations on a good system?

 

cheers

 

Edited by Michaelangelo999
Link to comment
Share on other sites

Hi Michael

Your house requires a system designed and installed to Grade A LD2 which is a full fire alarm system.

Your electricians are right not to get involved in something that will not conform to building regulations.

You should have been made aware of this at the design stage along with costs.

  • Upvote 2
  • Downvote 1
Link to comment
Share on other sites

1 minute ago, Simlec said:

Hi Michael

Your house requires a system designed and installed to Grade A LD2 which is a full fire alarm system.

Your electricians are right not to get involved in something that will not conform to building regulations.

You should have been made aware of this at the design stage along with costs.

 

Thanks, I was initially advised it needs Grade B, LD2 .. are you sure it's Grade A , The architect and BC both initially specc'd it at design stage as Grade B, and then...still at design stage they approved it to not require grade B such to allow it to be interlinked.

 

However A and B has a single point of failure in the central system (worse - if it set on fire itself, as rare as that may be) unlike battery backed up interlinked which has no single point of failure - so where I'm protecting my family I want the best solution and that's where BC have agreed interlinked is better for my situation.

 

Think of it like this...what is better, 10 security guards each with a megaphone and a walkie talkie (equivalent of interlinked) or 1 security guard with 9 CCTV screens and a megaphone (centralised system)?

 

It's somewhat a grey area for the electricians ... I agree, I just want a solution that is safe and best for my family and I simply have no good defense as to why for a one family dewlling that centralised is better than interlinked....I would welcome any defense here as I really would like someone to give a good reason why a robust interlinked is a worse solution to a cheaper centralised system?

 

 

Link to comment
Share on other sites

Thanks for that Simlec ! How bizarre that both specced/requested Grade B - i don't think there's much difference with Grade A (but will check exactly what). whilst reluctant for the reasons above, I'm likely going to centralised now anyway and will probably add in some standalone detectors for peace of mind, so hopefully grade A won't make too much difference..will find out.

 

Link to comment
Share on other sites

  • 2 weeks later...
36 minutes ago, firemonkey said:

Have you considered a small wireless fire alarm system? Something like a EMS Firecell - theres others out there and eliminates need for wiring once the spur is done

A bit pointless on a new build.

Link to comment
Share on other sites

Are you fitting cctv? Put a camera looking at the panel display if you want to see which detector activated without going to the panel, or fit some repeater displays around the house.

other alternative is wire the fire panels printer output to the nvrs serial port and set a camera up as POS capture.

Link to comment
Share on other sites

Fitted a couple of Rick O'Shea smokes the other day.

I quite like them, they are like having stand alone smokes but with the added benefit of the wireless.

I could see them being used for retrofitting in very small domestic max 3-4 points, even if the mesh drops off you have stand alone protection.

Would be nice if there was option for external power tho.

 

Link to comment
Share on other sites

  • 6 years later...
5 hours ago, Michaelangelo999 said:

What sort of answer is that ? - you’re meant to be a moderator…McModerator that’s as useful as a chocolate fireguard !

Not meant to be is a. Redirect your fireguard comment to admin. 

I have various models for sale some are chocolate but I prefer my barely used, one good owner never raced or rallied water ones. 

securitywarehouse Security Supplies from Security Warehouse

Trade Members please contact us for your TSI vetted trade discount.

Link to comment
Share on other sites

16 hours ago, sixwheeledbeast said:

So what happened 6 years later?

Hopefully, a stand alone fire system and not what the topic says...

Maybe bored in holidays going through emails...

Link to comment
Share on other sites

18 hours ago, sixwheeledbeast said:

So what happened 6 years later?

Hopefully, a stand alone fire system and not what the topic says...

TBF its only gonna be a problem if theres a fire and a fatality....😜

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.